I'm using the latest modbus driver V2.04 (July 8th, 2024) in my wire graph. I'm running in TCP mode. It works fine reading, but when writing, it returns a timeout, even though the value is written to the sever fine. I increased the timeout of the driver all the way to 20 seconds and it continues to occur. I tried it writing multiple registers to a float, and also single registers to a single integer register.
Error:
Reason: com.ghgande.j2mod.modbus.ModbusIOException: Executing transaction 53 B6 00 00 00 0B C8 10 03 47 00 02 04 3F 66 66 66 failed (tried 1 times) Socket timeout reading response - Read timed out
If I use Modbus Poll to write then it writes the value fine, shows success, and has the proper value under communications.
FC16 Mode
Tx:001948-07 79 00 00 00 0B C8 10 03 47 00 02 04 3F 66 66 66
Rx:001949-07 79 00 00 00 0B C8 10 03 47 00 02
Writing to a single register (integer). Fails with the same timeout.
Reason: com.ghgande.j2mod.modbus.ModbusIOException: Executing transaction 53 C4 00 00 00 09 C8 10 02 BB 00 01 02 00 01 failed (tried 1 times) Socket timeout reading response - Read timed out
Modbus Poll writes to it fine in FC6 Mode
Tx:001954-07 91 00 00 00 06 C8 06 02 BB 00 01
Rx:001955-07 91 00 00 00 06 C8 06 02 BB 00 01
In FC16 Mode:
Tx:001956-07 9D 00 00 00 09 C8 10 02 BB 00 01 02 00 01
Rx:001957-07 9D 00 00 00 09 C8 10 02 BB 00 01
Has anyone else reproduced this?